Lovely, thanks for the info killjoy13amp total over the two sockets, it's the rating limit on the cable feeding the sockets.
Right, I've just checked the circuit breaker box, and the upstairs sockets are protected by a 32A RCD and the downstairs by a separate 32A RCD.My flat has only one ring main around it and I routinely draw up to 32 amps from it.
.
Yes, and you can use both sockets of a twin with 13 amps from each.Right, I've just checked the circuit breaker box, and the upstairs sockets are protected by a 32A RCD and the downstairs by a separate 32A RCD.
So, I'm guessing two separate ring mains protected by a 32A RCD each.
Am I right in thinking that I can safely run appliances up to around 7.5Kw on each circuit, as long as I don't exceed 13 amps on a single socket?
I was tempted to reply with a tongue in cheek comment, but held myself back lol.Exercise your breakers every so often to make sure they will trip.
2.5mm T+E is the likely cable used to make your ring main or radial. The ring could run up to 27amps with said cable but a radial less so (i'm not sure how much less so..!). The 13amp double sockets are not fused and therefore the full current rated by the related breaker in your consumer unit is available at those sockets.On one of these household double sockets, is the max amps 13 amps per socket, or 13 amps shared between the two?